Troubleshooting
Operation/Control Troubles
Q1. Unable to operate the teaching box
- A1-1
- Check the connection of the teaching box. Is the teaching box connected properly?
- Check the screws.
- If they are not connected properly, connect and tighten the screws properly.
- A1-2
- Check if the select switch (R/T) of the controller is set to “T” (*Some controllers do not have the select switch. /*Some robots are terminal connection type).
- If not, select “T" and operate.
- Is RS232C cable connected?
- If so, disconnect the RS232C cable and operate.
- A1-3
- Is the controller select switch set to other than“0"? Is it set to the sequencer mode?
- If the select switch is set to other than "0", set to “0” and check again.
- A1-4
- Check if the cursor on the controller display is blinking.
- If not, contact JEL service section.
- If blinking, check if the robot is in operation. Please check the signals from the system.
Q2. Unable to control via sequencer
- A2-1
- Is the I/O cable connected properly?
- Check the connection of the I/O cable.
- If the cable is not connected, connect the cable properly and check again.
- A2-2
- Check if the I/O voltage and capacity are not over 24V. Or short?
- If it is not 24V, input properly and check again.
- A2-3
- Check if the compound command has been input (written to the controller)?
- If not, write the compound command data via software JEL DATA3 and check again.
- A2-4
- Check the controller select switch. Is “B” or “C” selected?
- If not, select “B” or “C” and check again.
- A2-5
- Check if both “READY” and “BUSY” signals are properly output. Turn the select switch to “C” and check the dot display.
- If "READY" is not displayed and “BUSY” signal has been output, check if the robot is in operation. Check the robot again.
- A2-6
- If "READY" is displayed, check if the alarm stop signal is not input.
- Check I/O, teaching box and external input.
Q3. Unable to communicate via RS232C
- A3-1
- Check if the RS232C communication cable is connected properly, not connected to RS485 port.
- If the cable is not connected to RS232C, connect properly and check again.
- A3-2
- Check if the controller select switch is set to “0”.
- If not, set to “0” and check again. (This may differ depending on the customer specs.)
- A3-3
- Check if teaching box is not connected, or it is not turned ON.
- If it is connected, or turned ON, disconnect and check again.
- A3-4
- Check if teaching box select switch is set to “R”.
- If“T” is selected, select “R”. (This may differ depending on the customer specs.)
- A3-5
- Check the COM port and baud rate (9600dps).
- If the setting is wrong, set it correctly.
- A3-6
- Check the robot body No.
- Communicate by the correct setting.
- If body No. is correct, turn the power OFF once, and check again.