Troubleshooting

Operation/Control Troubles

Q1. Unable to operate the teaching box

A1-1
Check the connection of the teaching box. Is the teaching box connected properly?
Check the screws.
If they are not connected properly, connect and tighten the screws properly.
A1-2
Check if the select switch (R/T) of the controller is set to “T” (*Some controllers do not have the select switch. /*Some robots are terminal connection type).
If not, select “T" and operate.
Is RS232C cable connected?
If so, disconnect the RS232C cable and operate.
A1-3
Is the controller select switch set to other than“0"? Is it set to the sequencer mode?
If the select switch is set to other than "0", set to “0” and check again.
A1-4
Check if the cursor on the controller display is blinking.
If not, contact JEL service section.
If blinking, check if the robot is in operation. Please check the signals from the system.

Q2. Unable to control via sequencer

A2-1
Is the I/O cable connected properly?
Check the connection of the I/O cable.
If the cable is not connected, connect the cable properly and check again.
A2-2
Check if the I/O voltage and capacity are not over 24V. Or short?
If it is not 24V, input properly and check again.
A2-3
Check if the compound command has been input (written to the controller)?
If not, write the compound command data via software JEL DATA3 and check again.
A2-4
Check the controller select switch. Is “B” or “C” selected?
If not, select “B” or “C” and check again.
A2-5
Check if both “READY” and “BUSY” signals are properly output. Turn the select switch to “C” and check the dot display.
If "READY" is not displayed and “BUSY” signal has been output, check if the robot is in operation. Check the robot again.
A2-6
If "READY" is displayed, check if the alarm stop signal is not input.
Check I/O, teaching box and external input.

Q3. Unable to communicate via RS232C

A3-1
Check if the RS232C communication cable is connected properly, not connected to RS485 port.
If the cable is not connected to RS232C, connect properly and check again.
A3-2
Check if the controller select switch is set to “0”.
If not, set to “0” and check again. (This may differ depending on the customer specs.)
A3-3
Check if teaching box is not connected, or it is not turned ON.
If it is connected, or turned ON, disconnect and check again.
A3-4
Check if teaching box select switch is set to “R”.
If“T” is selected, select “R”. (This may differ depending on the customer specs.)
A3-5
Check the COM port and baud rate (9600dps).
If the setting is wrong, set it correctly.
A3-6
Check the robot body No.
Communicate by the correct setting.
If body No. is correct, turn the power OFF once, and check again.