Troubleshooting

Initial Operation Troubles

Q1. Unable to turn the power on

A1-1
Is the controller power cable connected properly?
Check the main power supply.
If not, connect the cable properly. (Refer to the operation manual & spec book)
A1-2
Check if the connecting part is not loosened.
If the cable is loosened, connect properly.
A1-3
Check the power voltage and capacity.
Are the specified voltage and capacity stably supplied? (Refer to the spec book)
If the power is not stably supplied, supply properly. (Refer to the spec book)
A1-4
Check if the EMG terminal and REM terminal of the controller are openend.
If they are opened, close them and check again.
A1-5
Check if the stop signal is input from teaching box or external input (I/O or RS232C).
If it is input, release it and check again.
A1-6
Check the fuse of the power supply.

Q2. Unable to move the robot

A2-1
Check the serial number of the controller and the robot. (6-8 digits number) Are they the same?
If they are different, use the same serial number of the robot and the controller.
A2-2
Is the power connected properly? (Are both EMG terminal and REM terminal closed?)
If not, connect the power properly.
A2-3
Check if the cables between robot and controller are connected properly.
Disconnect them and connect again. Make sure that connection part is locked properly.
If cables are not connected, connect first and lock and check again.
A2-4
Check if the robot is excited. Move the robot softly by hand.
Robot moves. (It is not excited.)
Check if REM terminal of the controller is opened.
If it is opened, close REM terminal.
A2-5
Enter the command “$1” and check if “$100” is returned via RS232C communication.
If other status is returned, check the error code (refer to the operation manual), remove the cause, and check again.
A2-6
Check if the robot is initialized. Confirm the origin search (Command $1PT) has been completed.
Origin is set with 3-axis: 1101 / 4-axis: 1111/ 5-axis: 11111.
If origin is not set and the response "0000" is returned, execute the origin search.
A2-7
Check if the operation commands are correct.
If not, confirm the operation commands again.
A2-8
Check if the robot can be operated via teaching box.
If still enable to move the robot and to release the error, check the robot serial number and contact JEL service section.

Q3. Unable to communicate with the controller (for RS232C communication)

A3-1
Check if the RS232C communication cable is connected properly. *Make sure not to connect to RS485 port.
If the cable is not connected to RS232C, connect properly and check again.
A3-2
Check the select switch. Is "0" selected?
If not, select “0” and check again. (*This may differ depending on the customer specs.)
A3-3
Check if teaching box is not connected and it is not turned ON.
If it is connected, or it is turned ON, disconnect and check again.
A3-4
Check the R/T select switch. Is “R” selected?
If“T” is selected, select "R". (*This may differ depending on the customer specs.)
A3-5
Check the COM port and baud rate (9600dps).
If the setting is wrong, make sure to set it up correctly.
A3-6
Check the robot body No.
Make sure to set it up correctly.
If the body No. is correct, turn the power OFF and check again.

Q4. Unable to communicate with the controller (for PLC or parallel I/O)

A4-1
Check if the cable is connected properly to the PLC I/O.
If not, connect properly and check again.
A4-2
Check the select switch. Is “B” or “C” selected?
If“B” or “C” is not selected, select “B” or “C” and check again.
A4-3
Check if the PLC power is connected properly.
If not, connect properly and check again.
A4-4
Check if ready/busy signals are not always output. Check the ready/busy signals on the controller PLC monitor ”C”.
If signals are correct, check the robot serial number (6-8 digits number) and contact JEL service section.
When strobe is ON, check the system software.
When strobe is OFF, turn the teaching box off.